Question 3035 of 790 · California General Electrician Exam
A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3035
- B: 200 A
Explanation
The feeder OCPD must be at least 125 percent of the continuous load. 160 A times 1.25 is 200 A, which is a standard rating. See 215.3 and 240.6(A).
More questions: Feeders and Overcurrent Protection