Question 3033 of 790 · California General Electrician Exam
Under the 10 ft feeder tap rule, field-installed tap conductors that leave the enclosure must have an ampacity of at least what fraction of the feeder OCPD rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3033
- A: One-tenth
Explanation
Field-installed 10 ft taps that leave the enclosure where the tap is made must have an ampacity of at least one-tenth of the rating of the OCPD protecting the feeder. See 240.21(B)(1).
More questions: Feeders and Overcurrent Protection
- 3035A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?
- 3036In a multi-tenant building, who must have ready access to the OCPDs protecting the conductors supplying a tenant space?
- 3037Arc energy reduction is required where the highest continuous current trip setting of a circuit breaker is at least what value?
- 3039May an OCPD be placed in a grounded conductor?
- 3040Which statement about supplementary OCPDs is correct?
- 3041Unless specifically permitted elsewhere, what is the maximum OCPD for 10 AWG aluminum conductors?