Question 2025 of 790 · California General Electrician Exam
Using the 83 percent rule of the 2020 and 2023 NEC, what minimum aluminum XHHW conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2025
- B: 4/0 AWG
Explanation
200 A times 0.83 is 166 A. From Table 310.16, 75 degree C aluminum column, 4/0 is rated 180 A and 3/0 is only 155 A. See 310.12.