Under the 2020 and 2023 NEC, where must the emergency disconnect for a one-family dwelling be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2031
- B: In a readily accessible outdoor location
Explanation
Section 230.85 requires an emergency disconnect for one- and two-family dwelling services at a readily accessible outdoor location so first responders can shut off power without entering the building. This requirement first appeared in the 2020 edition.