Question 2032 of 790 · California General Electrician Exam
In a 120/240 volt single-phase dwelling service rated 200 A, the 2020 and 2023 NEC allow the service conductors to be sized at what percentage of the service rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2032
- D: 83 percent
Explanation
Section 310.12 permits service and main feeder conductors for 120/240 volt dwelling services up to 400 A to have an ampacity of not less than 83 percent of the service rating. This replaced the former table method.
More questions: Services and Service Equipment
- 2033What may be attached to a service mast that supports a service drop?
- 2034Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
- 2036What must be done with a service GFPE system when it is first installed?
- 2037What is the minimum height of working space for service equipment rated 1000 volts or less?
- 2038Under the 2023 and 2026 NEC, surge protection at the service is required for dwelling units and also for which of the following?
- 2039Service conductors installed under a building are considered outside the building when they are covered by at least how much concrete?