Question 2029 of 790 · California General Electrician Exam
Where must the service overcurrent device be located relative to the service disconnect?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2029
- A: Part of the service disconnect or immediately adjacent to it
Explanation
The service OCPD must be an integral part of the service disconnecting means or located immediately adjacent to it. See 230.91.
More questions: Services and Service Equipment
- 2030What is the maximum ground-fault trip setting permitted for service GFPE?
- 2031Under the 2020 and 2023 NEC, where must the emergency disconnect for a one-family dwelling be installed?
- 2032In a 120/240 volt single-phase dwelling service rated 200 A, the 2020 and 2023 NEC allow the service conductors to be sized at what percentage of the service rating?
- 2033What may be attached to a service mast that supports a service drop?
- 2034Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
- 2036What must be done with a service GFPE system when it is first installed?