Question 2024 of 790 · California General Electrician Exam
What is the minimum rating of the service disconnecting means for a one-family dwelling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2024
- B: 100 amperes, 3-wire
Explanation
For a one-family dwelling the service disconnect must be rated at least 100 amperes, 3-wire. Other installations generally need at least 60 amperes. See 230.79(C).
More questions: Services and Service Equipment
- 2025Using the 83 percent rule of the 2020 and 2023 NEC, what minimum aluminum XHHW conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
- 2026What is the minimum size aluminum conductor permitted for an underground service lateral serving a general load?
- 2027An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?
- 2028What is the minimum vertical clearance for overhead service conductors above a residential driveway when the voltage does not exceed 300 volts to ground?
- 2029Where must the service overcurrent device be located relative to the service disconnect?
- 2030What is the maximum ground-fault trip setting permitted for service GFPE?