A service supplies a small commercial building, not a dwelling, with more than two branch circuits. What is the minimum service disconnect rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- C: 60 amperes
Explanation
For installations other than one-circuit, two-circuit and one-family dwelling installations, the minimum service disconnect rating is 60 amperes. See 230.79(D).