Question 2021 of 790 · California General Electrician Exam
A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2021
- C: 190 A
Explanation
Service-entrance conductors must carry 125 percent of the continuous load plus 100 percent of the noncontinuous load. 120 A times 1.25 is 150 A, plus 40 A gives 190 A. See 230.42(A).
More questions: Services and Service Equipment
- 2022Under the 2020 and later editions, how must two to six service disconnects for one service be arranged?
- 2023A service supplies a small commercial building, not a dwelling, with more than two branch circuits. What is the minimum service disconnect rating?
- 2024What is the minimum rating of the service disconnecting means for a one-family dwelling?
- 2025Using the 83 percent rule of the 2020 and 2023 NEC, what minimum aluminum XHHW conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
- 2026What is the minimum size aluminum conductor permitted for an underground service lateral serving a general load?
- 2027An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?