A department store has 120 single-yoke receptacle outlets. What receptacle demand load applies under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12103
- C: 15,800 VA
Explanation
120 x 180 VA = 21,600 VA (220.14(I)). Non-dwelling receptacle loads take the first 10 kVA at 100 % and the rest at 50 %: 10,000 + 11,600 x 0.5 = 15,800 VA.