A store has 45 ft of show window. What lighting load is required for the window under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12105
- A: 9,000 VA
Explanation
Show window lighting counts at 200 VA per linear foot (220.43(A)): 45 x 200 = 9,000 VA.