Question 12102 of 790 · California General Electrician Exam

An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?

Exactly one answer is correct.

Show solution

Correct answer to question 12102

  • B: 22,110 VA

Explanation

Each unit is 900 x 3 VA + 4,500 VA = 7,200 VA, for 57,600 VA in total. With the dwelling demand factors: 3,000 + 54,600 VA x 0.35 = 22,110 VA.

Next to question ›