Question 12101 of 790 · California General Electrician Exam

Under NEC 2020/2023 220.60, a dwelling has 10 kW of electric heat and a 5,000 VA AC unit that do not run together. What load is used in the standard method?

Exactly one answer is correct.

Show solution

Correct answer to question 12101

  • A: 10,000 VA

Explanation

220.60 allows the smaller of two noncoincident loads to be dropped. The 10,000 VA heating load is the larger one and is used.

Next to question ›