Under the NEC 2020 or 2023 unit load table, what is the general lighting load for an 8,000 ft2 office?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12109
- A: 10,400 VA
Explanation
Offices take 1.3 VA per ft2 in the 2020 and 2023 unit load table (Table 220.12 in 2020, Table 220.42(A) in 2023): 8,000 x 1.3 = 10,400 VA. The 3.5 VA value is from older editions.