Optional method (NEC 2020/2023): a 1,500 ft2 dwelling with two small-appliance and one laundry circuit, a 10 kW range, 5 kW dryer and 4.5 kW water heater has six separately controlled 2 kW baseboard heaters and a 4,000 VA AC unit. What is the total calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12027
- C: 22,200 VA
Explanation
General loads = 28,500 VA, so 10,000 VA + 40 % of 18,500 VA = 17,400 VA (220.82(B)). Four or more separately controlled heating units count at 40 %: 12,000 x 0.40 = 4,800 VA, which exceeds the 4,000 VA AC (220.82(C)). Total 22,200 VA.