A 120/240 V service has a maximum unbalanced load of 280 A. What neutral load is used under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12090
- B: 256.0 A
Explanation
The portion of unbalanced load above 200 A may be taken at 70 % (220.61(B)): 200 + 80 x 0.70 = 256 A.