Question 12089 of 790 · California General Electrician Exam

A dwelling feeder includes a 6.4 kW range demand. What neutral load is assigned to it under the NEC 2020 or 2023?

Exactly one answer is correct.

Show solution

Correct answer to question 12089

  • A: 4,480 VA

Explanation

220.61(B) permits ranges and dryers to be taken at 70 % of their calculated load on the neutral: 6,400 x 0.70 = 4,480 VA.

Next to question ›