Question 12077 of 790 · California General Electrician Exam
Under the NEC 2023, a 24 A, 240 V EVSE (nameplate 5,760 VA) is added to a dwelling. What EVSE load is used in the load calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12077
- A: 7,200 VA
Explanation
220.57 of the 2023 edition requires the EVSE load at 7,200 W (VA) or the nameplate rating, whichever is larger. Since 5,760 VA is smaller, 7,200 VA is used.