What is the minimum ampere rating of the disconnecting means for a hermetic motor-compressor rated 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8051
- B: 115 percent of rated-load or branch-circuit selection current, whichever is greater
Explanation
Section 440.12(A)(1) requires the disconnect to have an ampere rating of at least 115 percent of the nameplate rated-load current or branch-circuit selection current, whichever is greater. A horsepower rating is also required, based on the rated-load and locked-rotor currents.