Which receptacles on a portable generator rated 15 kW or smaller must have GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8055
- C: 125 volt, 15 and 20 ampere receptacles
Explanation
Section 445.20 requires listed GFCI protection for the 125 volt, 15 and 20 ampere receptacle outlets on portable generators rated 15 kW or smaller. The protection can be integral to the generator or to the receptacles. The same section applies to bonded and unbonded generators.