Question 8025 of 790 · California General Electrician Exam
What must a motor disconnecting means clearly indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8025
- C: Whether it is in the open (off) or closed (on) position
Explanation
Section 430.104 requires the disconnecting means to plainly indicate whether it is open or closed. A worker can then verify the motor is isolated before servicing it.
More questions: Motors, HVAC, Generators and Transformers
- 8027What is the minimum rating of a motor controller?
- 8028Where must the disconnecting means for a motor control circuit be arranged?
- 8030Under the 2023 NEC, where are the general rules for Class 1 remote-control and signaling circuits, such as many motor control circuits, located?
- 8032What does the code letter on a motor nameplate indicate?
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?
- 8035A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?