A motor has a table full-load current of 22 A. Dual-element fuses are used for branch-circuit short-circuit protection. What is the maximum standard fuse size, applying the next higher size rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8017
- B: 40 A
Explanation
Table 430.52 allows 175 percent for dual-element fuses. 22 A times 1.75 equals 38.5 A, which is not a standard size, so the next higher standard size of 40 A is permitted.