A three-phase motor has a table full-load current of 40 A. What is the maximum inverse time breaker rating for its branch circuit, without using exceptions?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8016
- A: 100 A
Explanation
Table 430.52 permits 250 percent for an inverse time breaker. 40 A times 2.5 equals 100 A, which is a standard size. 50 A results from wrongly applying 125 percent.