Question 8013 of 790 · California General Electrician Exam
What is the maximum rating of a nontime delay fuse used for motor branch-circuit short-circuit and ground-fault protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8013
- B: 300 percent of full-load current
Explanation
Table 430.52 permits nontime delay fuses up to 300 percent of the table full-load current for most ac motors. These fuses have no time delay and need a higher rating to survive inrush.
More questions: Motors, HVAC, Generators and Transformers
- 8014What is the maximum setting of an instantaneous trip breaker for a squirrel cage motor other than Design B energy efficient?
- 8015The calculated motor short-circuit protection value does not match a standard size. What does 430.52 permit?
- 8016A three-phase motor has a table full-load current of 40 A. What is the maximum inverse time breaker rating for its branch circuit, without using exceptions?
- 8017A motor has a table full-load current of 22 A. Dual-element fuses are used for branch-circuit short-circuit protection. What is the maximum standard fuse size, applying the next higher size rule?
- 8020Where must a motor disconnecting means be located in relation to the motor and driven machinery?
- 8021What does the NEC mean when it says equipment is in sight from other equipment?