Question 8001 of 790 · California General Electrician Exam
Branch-circuit conductors supplying a single continuous-duty motor must have an ampacity of at least what percentage of the motor full-load current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8001
- A: 125 percent
Explanation
Section 430.22 requires conductors supplying a single continuous-duty motor to have an ampacity of at least 125 percent of the motor full-load current rating. The full-load current comes from the NEC tables, as 430.6(A)(1) requires.