A motor with a marked service factor of 1.15 needs a separate overload device. What is the maximum rating as a percentage of nameplate full-load current?

Exactly one answer is correct.

Show solution

Correct answer to question 8005

  • A: 125 percent

Explanation

Section 430.32(A)(1) allows 125 percent of nameplate current for motors with a service factor of 1.15 or more. The same 125 percent applies to motors with a marked temperature rise of 40 degrees C or less.