Question 8007 of 790 · California General Electrician Exam
A motor has a service factor of 1.0 and no temperature rise marking. What is the maximum overload rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8007
- C: 115 percent of nameplate current
Explanation
Section 430.32(A)(1) limits overloads to 115 percent of nameplate current for all motors that are not marked with a 1.15 or higher service factor or a temperature rise of 40 degrees C or less.
More questions: Motors, HVAC, Generators and Transformers
- 8008A motor with a service factor of 1.0 has a nameplate current of 20 A. What is the maximum separate overload setting under 430.32(A)(1)?
- 8009The overload selected at 125 percent is not enough to start a motor with a service factor of 1.15. What is the highest rating the next step permits?
- 8010How many overload units are required for a three-phase ac motor?
- 8011What is the maximum rating of an inverse time breaker used as motor branch-circuit short-circuit and ground-fault protection for a standard squirrel cage motor?
- 8012What is the maximum rating of a dual-element time-delay fuse used as motor branch-circuit short-circuit and ground-fault protection?
- 8013What is the maximum rating of a nontime delay fuse used for motor branch-circuit short-circuit and ground-fault protection?