Question 7035 of 790 · California General Electrician Exam
In a commercial building, a panelboard is supplied by a feeder from another panel. What must the panelboard be marked with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7035
- D: The identification and location of the source that supplies it
Explanation
Section 408.4(B) requires panelboards and switchboards supplied by a feeder in other than one- or two-family dwellings to be permanently marked with where the power supply originates. This helps workers find the correct disconnect quickly.
More questions: Equipment, Devices and Luminaires
- 7036In a panelboard supplied by a 4-wire delta system with a high leg, which phase position must the high leg occupy?
- 7037In a dwelling unit, where are overcurrent devices such as a panelboard not permitted?
- 7038Which type of luminaire is not permitted in a clothes closet?
- 7039What is the minimum clearance between a surface-mounted LED luminaire with a completely enclosed light source and the closet storage space?
- 7040A recessed LED luminaire with a completely enclosed light source is installed in a closet ceiling. What is the minimum clearance to the storage space?
- 7041A surface-mounted fluorescent luminaire is installed on a closet ceiling. What is the minimum clearance to the storage space?