Question 7036 of 790 · California General Electrician Exam
In a panelboard supplied by a 4-wire delta system with a high leg, which phase position must the high leg occupy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7036
- C: The B phase
Explanation
Section 408.3(E)(1) requires the phase with the higher voltage to ground on a 4-wire delta system to be the B phase in panelboards and switchboards. The high leg must also be identified, normally by orange marking.