Question 7034 of 790 · California General Electrician Exam
What is the maximum rating of the overcurrent device protecting a panelboard?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7034
- D: Not greater than the rating of the panelboard
Explanation
Section 408.36 requires each panelboard to be protected by an overcurrent device with a rating not greater than that of the panelboard. The device may be in the panelboard or ahead of it.