Question 6070 of 790 · California General Electrician Exam
Which is a permitted use of Type UF cable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6070
- B: Direct burial in the earth
Explanation
UF cable is permitted for direct burial when identified for that use and in wet, dry, or corrosive locations. It is prohibited as service-entrance cable and embedded in concrete. See 340.10 and 340.12.
More questions: Wiring Methods, Conductors and Boxes
- 6071Where rigid PVC conduit is exposed above grade and subject to physical damage, it must be
- 6001What is the minimum cover for direct burial cable under the general condition (not under a building, slab, or roadway), 600 V or less?
- 6002What is the minimum cover for rigid metal conduit or IMC under the general condition, 600 V or less?
- 6003What is the minimum cover for a nonmetallic raceway listed for direct burial without concrete encasement, general condition?
- 6004A dwelling unit 120 V, 20 A branch circuit with GFCI protection is run underground in UF cable. What is the minimum cover?
- 6005What is the minimum cover for direct burial cable installed under a 4 in thick concrete slab with no vehicular traffic that extends at least 6 in beyond the installation?