What is the minimum cover for rigid metal conduit or IMC under the general condition, 600 V or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6002
- B: 6 in
Explanation
RMC and IMC provide physical protection, so the minimum cover in the general location column is 6 in. See Table 300.5 in NEC 2020 and 2023; the underground installation rules are in 300.7 in NEC 2026.