The ampacity of NM cable conductors is generally determined using which temperature column?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6069
- A: 60 C
Explanation
NM cable conductors are rated 90 C, but the ampacity must be that of 60 C conductors. The 90 C rating may be used for adjustment and correction calculations. See 334.80.