Which location permits Type NM cable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6066
- B: Exposed and concealed work in normally dry locations
Explanation
NM cable is permitted in normally dry locations in one- and two-family dwellings and other permitted occupancies. It may not be used as service-entrance cable, embedded in masonry or concrete, or in wet or damp locations. See 334.10 and 334.12.