Question 6051 of 790 · California General Electrician Exam
For an angle pull, a trade size 3 and a trade size 2 conduit enter the same wall of a pull box. What is the minimum distance to the opposite wall?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6051
- C: 20 in
Explanation
For angle pulls, the distance is 6 times the largest raceway plus the sum of the other raceways on the same wall: 6 x 3 + 2 = 20 in. See 314.28(A)(2).