Question 6054 of 790 · California General Electrician Exam
What does the designation THHN indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6054
- B: Thermoplastic, high heat 90 C, nylon jacket, dry and damp locations
Explanation
THHN is a thermoplastic insulation rated 90 C for dry and damp locations with a nylon outer jacket. The double H means high heat resistance (90 C), and N means nylon. See Table 310.4(1) in NEC 2020 and 2023.
More questions: Wiring Methods, Conductors and Boxes
- 6055What is the temperature rating of THWN-2 insulation in a wet location?
- 6056XHHW insulation, without the -2 suffix, is rated 90 C in dry and damp locations and what in wet locations?
- 6057Which location is classified as a wet location?
- 6058In NEC 2020 and 2023, aluminum, copper-clad aluminum, or copper conductors may be run in parallel only when they are
- 6063Which use of a flexible cord is prohibited?
- 6066Which location permits Type NM cable?