For a straight pull through a pull box containing 4 AWG or larger conductors, the box length must be at least how many times the largest raceway trade size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6050
- B: 8 times
Explanation
In straight pulls, the length of the box must be not less than 8 times the trade size of the largest raceway. See 314.28(A)(1).