A conduit run between two boxes has two 90 degree bends and four 30 degree offset bends. How many more degrees of bend may be added before a pull point is required?

Exactly one answer is correct.

Show solution

Correct answer to question 6035

  • C: 60 degrees

Explanation

The run already has 2 x 90 + 4 x 30 = 300 degrees. The limit between pull points is 360 degrees, so only 60 degrees more may be added. See the bend rules in the raceway articles (300.24 in NEC 2026).