Question 6040 of 790 · California General Electrician Exam
What volume allowance does the box fill table assign to each 12 AWG conductor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6040
- D: 2.25 cu in
Explanation
Table 314.16(B) assigns 2.25 cu in to each 12 AWG conductor, 2.00 cu in to 14 AWG, and 2.50 cu in to 10 AWG. Each conductor that originates outside the box and terminates or is spliced inside counts once.