Question 6011 of 1003 · California General Electrician Exam
How does the Code classify the interior of an underground raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6011
- C: As a wet location
Explanation
The interior of enclosures or raceways installed underground is a wet location, so conductors must be listed for wet locations, such as THWN or XHHW. See 300.5(B) in NEC 2020 and 2023 (300.7(B) in NEC 2026).
More questions: Wiring Methods, Conductors and Boxes
- 6012When a cable is installed through a bored hole in a wood stud, how far must the edge of the hole be from the nearest edge of the stud unless a steel plate is used?
- 6013NM cable passes through holes in metal studs that are punched at the factory. What must be done?
- 6014A cable run parallel to a wood framing member must be kept at least how far from the nearest edge of the member where nails or screws are likely to penetrate?
- 6015Under NEC 2020 and 2023, a cable run under metal-corrugated sheet roof decking must be kept at least how far from the lowest surface of the decking?
- 6017Where ungrounded conductors 4 AWG or larger enter an enclosure through a raceway, what is required at the entry?
- 6019EMT must be securely fastened within what distance of each outlet box, junction box, or termination?