Question 6013 of 790 · California General Electrician Exam
NM cable passes through holes in metal studs that are punched at the factory. What must be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6013
- A: Protect the cable with listed bushings or grommets
Explanation
Where NM cable passes through openings in metal framing, it must be protected by listed bushings or grommets securely fastened in the opening before the cable is installed. See 300.4 in NEC 2020 and 2023 (300.6 in NEC 2026).
More questions: Wiring Methods, Conductors and Boxes
- 6014A cable run parallel to a wood framing member must be kept at least how far from the nearest edge of the member where nails or screws are likely to penetrate?
- 6015Under NEC 2020 and 2023, a cable run under metal-corrugated sheet roof decking must be kept at least how far from the lowest surface of the decking?
- 6017Where ungrounded conductors 4 AWG or larger enter an enclosure through a raceway, what is required at the entry?
- 6019EMT must be securely fastened within what distance of each outlet box, junction box, or termination?
- 6020What is the maximum distance between supports for EMT under the general rule?
- 6021Rigid metal conduit must generally be secured within what distance of each box or termination?