When a cable is installed through a bored hole in a wood stud, how far must the edge of the hole be from the nearest edge of the stud unless a steel plate is used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6012
- D: 1 1/4 in
Explanation
Holes in wood framing must be bored so the edge of the hole is at least 1 1/4 in from the nearest edge of the member. If that distance cannot be kept, the cable must be protected by a steel plate or sleeve. See 300.4 in NEC 2020 and 2023 (300.6 in NEC 2026).