Question 5031 of 790 · California General Electrician Exam
What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5031
- C: 2 AWG
Explanation
The main bonding jumper is sized from Table 250.102(C)(1) based on the largest ungrounded service conductor. For copper over 3/0 through 350 kcmil the jumper must be at least 2 AWG copper. See 250.28(D).
More questions: Grounding and Bonding
- 5032A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?
- 5033A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?
- 5034For a grounded service, the GEC connection to the grounded service conductor is permitted
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?
- 5036What is the minimum copper equipment grounding conductor for a feeder protected by a 100 A OCPD?
- 5037What is the minimum copper equipment grounding conductor for a feeder protected by a 400 A OCPD?