What is the minimum branch circuit rating for a household range rated 8 3/4 kW or more?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4092
- B: 40 amperes
Explanation
210.19 sets 40 amperes as the minimum branch circuit rating for household ranges of 8 3/4 kW or more. The actual size is based on the demand load for the range.