Question 3028 of 790 · California General Electrician Exam
Three parallel sets of conductors give a total ampacity of 1140 A. What is the largest standard OCPD permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3028
- C: 1000 A
Explanation
Above 800 A the next size up rule does not apply, so the OCPD must not exceed the conductor ampacity. The largest standard rating not over 1140 A is 1000 A. See 240.4(C) and 240.6(A).
More questions: Feeders and Overcurrent Protection
- 3029Which standard OCPD rating comes directly after 800 A?
- 3030A circuit breaker has an interrupting rating other than what value must be marked with that rating?
- 3031When is a 1200 A feeder disconnect on a 480Y/277 volt system not required to have its own GFPE?
- 3032What is the length limit for outside feeder tap conductors that terminate at a single OCPD that is part of or next to the building disconnect?
- 3033Under the 10 ft feeder tap rule, field-installed tap conductors that leave the enclosure must have an ampacity of at least what fraction of the feeder OCPD rating?
- 3035A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?