Question 13108 of 790 · California General Electrician Exam

A 15 kVA, single-phase transformer with a 240 volt primary is protected on the primary side only. Which statement about its primary current is correct?

Exactly one answer is correct.

Show solution

Correct answer to question 13108

  • D: It is 62.5 A, so the 125 % primary rule applies

Explanation

Primary current is 15,000 / 240 = 62.5 A. Because that is 9 A or more, primary-only protection uses 125 %; the 167 % and 300 % limits apply only to primary currents below 9 A and below 2 A.