A branch circuit supplies 30 A of continuous load and 20 A of noncontinuous load. What is the minimum standard overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13111
- C: 60 A
Explanation
The minimum is 125 % of the continuous load plus 100 % of the noncontinuous load: 30 x 1.25 + 20 = 57.5 A, so the next standard size is 60 A. Applying 125 % to the whole 50 A gives 62.5 A, which is not a standard size and leads to 70 A.