What is the maximum continuous lighting load in volt-amperes on a 277 volt, 20 A branch circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13113
- A: 4,432 VA
Explanation
The continuous load is limited to 80 % of 20 A = 16 A, and 16 x 277 = 4,432 VA. 5,540 VA uses the full 20 A, and 1,920 VA uses 120 V.
More questions: Electrical Calculations
- 13114How many 277 volt LED luminaires drawing 0.75 A each may be connected to a 20 A branch circuit if they operate continuously?
- 13115A three-phase feeder supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum standard overcurrent device rating?
- 13116A 24 A continuous load is supplied by a branch circuit. What is the minimum overcurrent device rating and minimum copper conductor size with 60 °C terminations?
- 13118A single-phase 240 volt, 10 kW heater operates for 3 hours. How many kilowatt-hours does it use, and what is its current?
- 13119What is the circular mil area of a 10 AWG conductor as listed in Chapter 9 Table 8?