Question 13072 of 790 · California General Electrician Exam
A 3 inch by 2 inch by 3-1/2 inch device box is rated 18.0 cu in. It holds a switch, two 14 AWG cables with grounds (4 insulated conductors) and internal clamps. How many additional 14 AWG insulated conductors may be added?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13072
- D: 1
Explanation
Current count: 4 conductors + 1 grounding + 1 clamps + 2 yoke = 8, and 8 x 2.0 = 16.0 cu in. The remaining 2.0 cu in allows exactly 1 more 14 AWG conductor.
More questions: Electrical Calculations