Question 13073 of 790 · California General Electrician Exam
A conductor runs unbroken through a box without being spliced or terminated and is not looped. How is it counted for box fill?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13073
- A: As one conductor
Explanation
An unbroken conductor that passes through a box counts once. Only an unbroken conductor looped at least twice the length required for free conductors counts twice.
More questions: Electrical Calculations
- 13074What is the maximum fill percentage for a raceway that contains three or more conductors, other than a short nipple?
- 13075What maximum fill percentage applies when exactly two conductors are installed in a raceway?
- 13076A raceway nipple not exceeding 24 inches long between enclosures may be filled to what percentage?
- 13077Using a 40 % fill area of 0.213 sq in for 3/4 inch EMT and an area of 0.0133 sq in for 12 AWG THHN, how many 12 AWG THHN conductors are permitted?
- 13078How many 10 AWG THHN conductors (0.0211 sq in each) may be installed in 1/2 inch EMT, which has a 40 % fill area of 0.122 sq in?
- 13079Three 4 AWG THHN (0.0824 sq in each) and one 8 AWG THHN (0.0366 sq in) are to be installed in EMT. Which is the smallest trade size permitted? (40 % areas: 3/4 in 0.213, 1 in 0.346, 1-1/4 in 0.598 sq in)